The installation guide for miniature gear flowmeters:


I. Flow Direction & Orientation Control (Critical Steps)?


Verify Flow Direction Marking?

The arrow indicator on the flowmeter housing ?must strictly align? with the actual fluid flow direction in the pipeline. Reverse installation causes gear backlash, measurement failure, or device damage?.

→ ?Operational Validation?: After installation, apply low-pressure air blast at the inlet; normal pulse signal changes on the display confirm correct orientation?.


Installation Orientation Standards?


Horizontal Installation (Preferred)?: Ensure the elliptical gear shaft is parallel to ground level, with the cover plate perpendicular to the horizontal plane?.

Vertical Installation?: Permit ?bottom-to-top flow only? to prevent gear jamming?.

II. Gear Assembly Key Details?


Magnetic Pole Calibration?

Magnetically coupled gears must be installed with the magnetic pole surface facing ?upward?, aligned with the Hirsemann connector?.

→ ?Test Requirement?: Manually rotate gears to confirm smooth meshing without binding?.


Leak Prevention?

Tighten cover plate screws following a ?cross-diagonal sequence? to avoid seal deformation?.


III. Pipeline System Protection?

Mandatory Filtration?

Install a filter upstream of the flowmeter to block fibers and particulates from entering gear clearance?.

Bypass Pipeline Design?

Deploy a bypass circuit for vertical installations or maintenance requirements?.

Valve Positioning?

Regulating valves must be installed ?downstream?; operate valves gradually during startup/shutdown?.

IV. Environmental & Electrical Safety?

Vibration/Interference Mitigation?

Isolate from strong magnetic sources (motors, transformers); reinforce piping if vibrating?.

Electrical Isolation?

Use shielded cables with single-point grounding (resistance <10 ohm)?.

Corrosion Protection?

Select stainless steel flowmeters for corrosive fluids?.

V. Pre-Commissioning Checklist?

text

Copy Code

1. Flush pipelines: Remove welding slag/debris (mandatory for new pipelines)?:ml-citation{ref="6" data="citationList"}.  

2. Seal test: Pressure-check all connections for leaks.  

3. No-flow test: Verify display shows zero reading without fluid.  

4. Minimum flow test: Confirm stable pulse signals at low flow rates?:ml-citation{ref="1,2" data="citationList"}.  



?? PROHIBITED OPERATIONS?:


Direct steam flushing of flowmeter?.

Exceeding rated capacity (recommended flow range: 50%–80%)?.


Following these procedures ensures measurement accuracy and extends service life. For gear seizure incidents, disassemble, clean, and recalibrate magnetic pole alignment?.


Key Terminology Consistency:

旁通管道 → Bypass pipeline

赫斯曼接頭 → Hirsemann connector

磁極 → Magnetic pole

對角線順序 → Cross-diagonal sequence

脈沖信號 → Pulse signal


主站蜘蛛池模板: 会同县| 海城市| 乐安县| 永年县| 漯河市| 榆中县| 双江| 永寿县| 盈江县| 大厂| 三江| 伊宁县| 红河县| 绍兴县| 土默特右旗| 邵阳市| 嫩江县| 米易县| 托克托县| 开江县| 平邑县| 阿克苏市| 巨野县| 福建省| 封开县| 康乐县| 永宁县| 贺兰县| 马龙县| 图片| 广西| 常德市| 布尔津县| 宕昌县| 乐亭县| 昌黎县| 张家港市| 凌海市| 大新县| 磐石市| 万全县| 长沙县| 新干县| 永康市| 湘潭市| 五指山市| 昭通市| 威远县| 天等县| 浏阳市| 雅安市| 神农架林区| 册亨县| 内丘县| 威宁| 百色市| 霍邱县| 光山县| 呈贡县| 黔西| 涪陵区| 四平市| 大荔县| 九寨沟县| 南平市| 比如县| 大悟县| 连江县| 镇安县| 清丰县| 郁南县| 西昌市| 名山县| 古蔺县| 茌平县| 灵山县| 柳州市| 永福县| 徐汇区| 祁东县| 巴林左旗| 林甸县|